Working with SGT-700, i recently observed this strange phenomenon of the GTG Air Filter Dp falling (0.51 to 0.42kPa) after there was slight drizzle. Falling Dp can be caused by either
A) HP side falling: Ruled out - 04 Trasnmitters monitoring the Dp showed same behaviour
B) LP side Rising: Probable, which would imply the resistance across the filters actually reduced
C) Any other possibilty?
But is this possible? Has Anyone observed a similar thing?
----------------------------------------------------------------------------
TREND LEGEND
Black Line - Single DP Transmitter across first stage Jet Pulse Filters
Red Line - Three (2oo3) DP Transmitter across entire Air Intake (Jet Pulse + HEPA)
Blue Line - Ambient Humidity
Olive Line - Ambient Temperature
A) HP side falling: Ruled out - 04 Trasnmitters monitoring the Dp showed same behaviour
B) LP side Rising: Probable, which would imply the resistance across the filters actually reduced
C) Any other possibilty?
But is this possible? Has Anyone observed a similar thing?
----------------------------------------------------------------------------