Thread Starter

maria

Hi,

i want s7-200 micro/win32 software and its output display on PC when we use PLC on temperature control.
 
W

Waleed El-Badry

Hello,

Do you have an analog module to take the analog voltage from?

Siemens S7-200 CPU 222 or CPU 224 comes with a digital IO only, so you must have an analog module to be able to get the analog voltage.

Second of all, please read the data sheet of PLC as it has the instruction for reading from analog input (AIWx).

MicroWin is used to download, upload your S7-200 program. It is a bad practice to use it as a HMI.

There are many HMI software available, but you must have an OPC Server to connect your PLC to it.

If you need further assistance, just let me know.

Have a lovely day.

Waleed El-Badry