Siemens Sentron PAC3200 Power Meter Energy Readings
T
Terence Ng
How can I retrieve the energy reading from Siemens Sentron PAC3200 power meter which is Double Register format? I'm using WINPM.Net Software equipvalent to IOn Enterprise from Power Measurement Schneider. How can I break the double register to smaller register such as 16 or 32 bits in order to get the right result?
E
Elmer Bulman
These double registers are most likely IEEE Single Precision numbers. As such, they will be sent in one of 4 possible byte orders.
1) B0 B1 B2 B3
2) B1 B0 B3 B2
3) B2 B3 B0 B1
4) B3 B2 B1 B0
Your equipment should have a selection of options to decode the proper numbers. Google IEEE Single Precision for bit assignments of float point numbers.
Here are some IEEE Single Precision examples:
B0 B1 B2 B3
1.000 = 0x3f 80 00 00
1.100 = 0x3f 8c cc cd
10.00 = 0x41 20 00 00
10.10 = 0x41 21 99 9a
T
If my master does not support 64 bits register, how can I break 64 bits into either 16 bits or 32 bits in order to get the readings? HOw to define the Bits on easy way?
May I know the difference between the KVAh app. Energy and Kwh readings on the Siemens Sentron PAC3200 Power meter, as I am interested in knowing my daily plant energy consumption.
regards,
Dan