taking data from quantum plc modbus tcp in dh+ net

S

Thread Starter

sunil rathaur

Sir,

we have dh+ network of ab plc 5/60 standard. recently we have installed Quantum DCS with Modbus tcp/ip . we would like to bring its data on dh+ bus in the main administrative building located at 1 km away and show it on PC with Rs view 32 HMI. please tell us how to go for it in the simple and cheapest way.
 
W

Wassim Daoud

You can do this easily with OPC. All you need is OPC Data Manager to connect both systems together.

http://www.matrikonopc.com/products/opc-data-management/opc-data-manager.aspx

You might also need an OPC Server for each protocol as well. If you don't have them, download them from here for free:

Modbus OPC Server:
http://www.matrikonopc.com/opc-drivers/opc-modbus/base-driver-details.aspx

Allen Bradley OPC Server:
http://www.matrikonopc.com/opc-drivers/opc-Allen-Bradley/base-driver-details.aspx

Hope this was helpful

Cheers,
Wassim
 
J

James Ingraham

GridConnect / FactoryComm has the PKV6000 Modbus TCP to Data Highway Plus gateway. Sounds like a perfect fit. Also much easier than trying to maintain a PC with an OPC bridge.
http://www.factorycomm.com/gc-pkv4500-mbtcpdhp.html

Fieldserver also has an Ethernet to DH+ Gateway, but they don't specify that it's Modbus/TCP.

DataLink Technologies has the GW1000-MODTCP Modbus/TCP to DH+ gateway.
http://www.datatechgateways.com/gw1000-modtcp/

I'd have sworn SST / Woodhead / Brad / Molex had one, but I can only find the Ethernet to Profibus, not DH+.

I've never tried any of these products.

-James Ingraham