Hello everyone,
I am currently servicing a self cleaning (pulse) inlet air filter system that has been having some issues. Since being operation began in 2019 the self cleaning system has not been automatically activated once. In 2023 the filters were checked and upon visual inspection they were ready to be replaced, however the dp across the filters hadn't reached the threshold to activate the cleaning system. Since then the system has been ran manually every month for 2 hours.
The system is setup to activate at a dp of 3 inches of H2O and then turn off at 2.5 inches of H2O, but I can't seem to find where those numbers came from (I joined the company fairly recently). The filter is an altair PRO cartridge filter and it is a clearcurrent air pulse system.
I have been unable to find any information from the manufacturers on how often should the pulse system run? What should the setpoint be for the dp? How significant of a differential pressure drop across the filters is expected after the pulse system runs? what is the life expectancy of the altair pro cartridge filter? Should the system run during gas turbine operation or when the Turbine is not running?
If anyone has any relevant information I would appreciate the help. The manufactures have not been very helpful.
Thank you.
I am currently servicing a self cleaning (pulse) inlet air filter system that has been having some issues. Since being operation began in 2019 the self cleaning system has not been automatically activated once. In 2023 the filters were checked and upon visual inspection they were ready to be replaced, however the dp across the filters hadn't reached the threshold to activate the cleaning system. Since then the system has been ran manually every month for 2 hours.
The system is setup to activate at a dp of 3 inches of H2O and then turn off at 2.5 inches of H2O, but I can't seem to find where those numbers came from (I joined the company fairly recently). The filter is an altair PRO cartridge filter and it is a clearcurrent air pulse system.
I have been unable to find any information from the manufacturers on how often should the pulse system run? What should the setpoint be for the dp? How significant of a differential pressure drop across the filters is expected after the pulse system runs? what is the life expectancy of the altair pro cartridge filter? Should the system run during gas turbine operation or when the Turbine is not running?
If anyone has any relevant information I would appreciate the help. The manufactures have not been very helpful.
Thank you.