I
Our gas turbine frame 6 ,Mark-V control TMR application was shut down on 05.01.2011 at 21:00 PM for offline water wash.
The following sequence occurred at 07:48 AM at 06.01.2011 while water wash job was under progress
07:35:23:000 1 L1START CPB
07:35:23:062 1 L1X
07:35:23:062 1 L20FG1X
07:35:23:062 1 L20FGX
07:35:23:062 1 L3MCSTR
07:35:23:062 1 L4
07:35:24:000 0 L1START CPB
07:37:30:812 1 L28FDA
07:37:30:875 0 L28FDA
07:37:38:187 0 L14HR
07:37:38:187 1 L20TV1X
07:37:41:093 1 Q 0380
07:37:54:062 1 L14HT
07:38:08:093 1 Q 0400
07:38:33:312 1 L14HM
07:39:33:187 1 L2TV
07:46:37:312 1 L28FDA
07:46:37:375 0 L28FDA
07:48:24:812 0 L1X
07:48:24:812 0 L20FG1X
07:48:24:812 0 L20FGX
07:48:24:812 0 L2TV
07:48:24:812 0 L3MCSTR
07:48:24:812 0 L4
07:48:24:812 1 L4T
07:48:25:093 1 Q 0093
07:48:25:093 1 Q 0378
07:48:25:750 0 Q 0093
AT THIS JUNCTURE m/c tripped however the i/o comm alarm was coming since 31.12.2010 intermittently(thrice) & got reset immediately without tripping the m/c. Flame detector A is toggling so, this point can be nullified.We are not able to track why L4T appeared. Can communication failure be a cause for tripping? if so, how to rectify the same.
The following sequence occurred at 07:48 AM at 06.01.2011 while water wash job was under progress
07:35:23:000 1 L1START CPB
07:35:23:062 1 L1X
07:35:23:062 1 L20FG1X
07:35:23:062 1 L20FGX
07:35:23:062 1 L3MCSTR
07:35:23:062 1 L4
07:35:24:000 0 L1START CPB
07:37:30:812 1 L28FDA
07:37:30:875 0 L28FDA
07:37:38:187 0 L14HR
07:37:38:187 1 L20TV1X
07:37:41:093 1 Q 0380
07:37:54:062 1 L14HT
07:38:08:093 1 Q 0400
07:38:33:312 1 L14HM
07:39:33:187 1 L2TV
07:46:37:312 1 L28FDA
07:46:37:375 0 L28FDA
07:48:24:812 0 L1X
07:48:24:812 0 L20FG1X
07:48:24:812 0 L20FGX
07:48:24:812 0 L2TV
07:48:24:812 0 L3MCSTR
07:48:24:812 0 L4
07:48:24:812 1 L4T
07:48:25:093 1 Q 0093
07:48:25:093 1 Q 0378
07:48:25:750 0 Q 0093
AT THIS JUNCTURE m/c tripped however the i/o comm alarm was coming since 31.12.2010 intermittently(thrice) & got reset immediately without tripping the m/c. Flame detector A is toggling so, this point can be nullified.We are not able to track why L4T appeared. Can communication failure be a cause for tripping? if so, how to rectify the same.