ABB REX640 modbus to be added to Schneider Power Monitoring Expert

Hello,

I have an issue with my relay ABB REX640, I would like to add this device to the Power monitoring expert software but it's not communicating. I tried the modbus poll and it has communication. Any idea on what is causing the issue?

Thank you everyone.
 
Does the software show a reason it's not communicating, such as an error message or error code?

Please also post the settings you've configured in Modbus Poll to establish successful communications and the current settings you are trying to use in Schneider Power Monitoring Expert.
 
Does the software show a reason it's not communicating, such as an error message or error code?

Please also post the settings you've configured in Modbus Poll to establish successful communications and the current settings you are trying to use in Schneider Power Monitoring Expert.
Hi,

Thank you for the reply, kindly see attached photos for the modbus poll settings.
1765821909146.png
1765821967499.png
1765822020925.png
 
In the StruxureWare Management Console, click on the Tools menu and select System > Diagnostics Viewer to find more information about why the status is marked as "Failure".
 
You confirmed that the REX640 is setup correctly for Modbus communication by successfully communicating to it from Modbus Poll.

Your issue most likely lies in the configuration of the Schneider Power Monitoring Expert software.

I'm sorry, but I have never actually used this Schneider software and am not familiar with it. The only knowledge I have is based on the user manual (https://download.schneider-electric...Type=User+guide&p_File_Name=7EN02-0348-00.pdf). Therefore, I'm afraid I may not be of any additional help in setting up this software.

Perhaps someone else is more familiar and will chime in.
 
You confirmed that the REX640 is setup correctly for Modbus communication by successfully communicating to it from Modbus Poll.

Your issue most likely lies in the configuration of the Schneider Power Monitoring Expert software.

I'm sorry, but I have never actually used this Schneider software and am not familiar with it. The only knowledge I have is based on the user manual (https://download.schneider-electric...Type=User+guide&p_File_Name=7EN02-0348-00.pdf). Therefore, I'm afraid I may not be of any additional help in setting up this software.

Perhaps someone else is more familiar and will chime in.
Thank you very much for your assistance.
Atleast now I know that thr REX640 modbus communication is ok.
 
A little more Google searching...

In your Diagnostics Viewer screenshot, I noticed it shows a RequestStatus of "blocked". Here is what Schneider's troubleshooting guide (https://product-help.schneider-elec..._troubleshooting/tools/diagnostics_viewer.htm) says about that:
blocked – The Log Inserter requires configuration information but all available resources are in use. By default, the Log Inserter can simultaneously request only up to 2 trees per site and 6 trees in total. The Request Update Time value indicates how long the request has been pending.
Additionally, the Comments column shows "Tree in use by GROUP1.REX640-not-clean". This is another hint as to the underlying issue. From the same document as above:
If the client's name ends with -not-clean, the node is currently being evaluated by Treemon/Validator.
So perhaps there is an issue with your device tree file or perhaps changes to the device tree file were made that have not yet been synchronized with the StruxureWare Management Console. Here's what Google AI spits out regarding this:
To resolve this status and synchronize the device configuration, you generally need to perform a retrieve or verify configuration action within the Management Console.

Resolution Steps (General)

Specific steps may vary slightly depending on whether you are using StruxureWare Data Center Expert or Power Monitoring Expert, but the general process involves retrieving the current configuration from the device:

  1. Navigate to the device in the device tree within the Monitoring perspective of the StruxureWare client.
  2. Right-click on the device that shows the "-not-clean" status.
  3. Select an option such as "Retrieve Device Settings" or "Verify Configuration" from the context menu. This action prompts the software to communicate with the physical device and download its current configuration parameters.
  4. Monitor the status in the configuration status pane or log. The status should change to "Complete" or "Verified" after the process is finished, and the "-not-clean" flag should be removed.
 
A little more Google searching...

In your Diagnostics Viewer screenshot, I noticed it shows a RequestStatus of "blocked". Here is what Schneider's troubleshooting guide (https://product-help.schneider-elec..._troubleshooting/tools/diagnostics_viewer.htm) says about that:


Additionally, the Comments column shows "Tree in use by GROUP1.REX640-not-clean". This is another hint as to the underlying issue. From the same document as above:


So perhaps there is an issue with your device tree file or perhaps changes to the device tree file were made that have not yet been synchronized with the StruxureWare Management Console. Here's what Google AI spits out regarding this:
Hi,

Thank you so much for the suggestions.

Most of the options shown is not available, so I also searched in AI
1766001487806.png
I'll start all over again.

I deleted all the files under treemon.exe related to rex640.

I'll update you if it is successful.
 
A little more Google searching...

In your Diagnostics Viewer screenshot, I noticed it shows a RequestStatus of "blocked". Here is what Schneider's troubleshooting guide (https://product-help.schneider-elec..._troubleshooting/tools/diagnostics_viewer.htm) says about that:


Additionally, the Comments column shows "Tree in use by GROUP1.REX640-not-clean". This is another hint as to the underlying issue. From the same document as above:


So perhaps there is an issue with your device tree file or perhaps changes to the device tree file were made that have not yet been synchronized with the StruxureWare Management Console. Here's what Google AI spits out regarding this:
Hi,

After deleting the old files and again creating a new modbus device, I got a different error message. Different from "tree not clean"
Possibly there are missing steps in my procedure or settings that needs to be configured.
 

Attachments

As I said I'm not familiar with the Schneider software, but to me it seems you may be reading data from the REX640 by reading coils (function code 0x01) in Modbus Poll, but in the Schneider software it seems you may be attempting to read data by reading registers (e.g. Holding Registers using function code 0x03) and looking at specific bits in those registers. This is not the same thing.
 
As I said I'm not familiar with the Schneider software, but to me it seems you may be reading data from the REX640 by reading coils (function code 0x01) in Modbus Poll, but in the Schneider software it seems you may be attempting to read data by reading registers (e.g. Holding Registers using function code 0x03) and looking at specific bits in those registers. This is not the same thing.
Hi,

Thanks again, I'll try to change registers.
 
If your ABB REX640 works in Modbus Poll but not in PME, the problem is likely configuration, not hardware. First, check that the baud rate, parity, stop bits, and node address match exactly. PME needs the correct driver or device template to read registers. Sometimes, a custom Modbus device is required in PME. Also, confirm that PME supports the function codes your relay uses. Timeout or polling settings can also block communication. Firmware versions may affect compatibility. For practical reference, you can study PCB projects like this Modbus to MQTT board. It shows how Modbus devices communicate with monitoring systems. Use it to understand register mapping and polling. Start by testing simple registers first. Adjust PME settings gradually. Logs in PME often show useful error details. This approach usually solves Modbus integration issues efficiently.
 
If your ABB REX640 works in Modbus Poll but not in PME, the problem is likely configuration, not hardware. First, check that the baud rate, parity, stop bits, and node address match exactly. PME needs the correct driver or device template to read registers. Sometimes, a custom Modbus device is required in PME. Also, confirm that PME supports the function codes your relay uses. Timeout or polling settings can also block communication. Firmware versions may affect compatibility. For practical reference, you can study PCB projects like this Modbus to MQTT board. It shows how Modbus devices communicate with monitoring systems. Use it to understand register mapping and polling. Start by testing simple registers first. Adjust PME settings gradually. Logs in PME often show useful error details. This approach usually solves Modbus integration issues efficiently.
Hi,

Thank you very much for the suggestions. I'll try it out
 