Single-loop controllers and PLC

A

Thread Starter

Anonymous

Which one is better to design a process plant which has several PID controlling loops:

1) Connect all loops to the plant PLC, do some PID programming, and let the PLC control the loops directly.

2) Utilise single-loop controllers (with PID capability) for every single loop, then integrate them to the plant PLC using communication scheme such as MODBUS, etc.
 
M

Marcos Thoni Bergamo

Mr. Anonymous,

Some positive points for the PLC solution:
. You may have a faster PID update cicle (compared to low-cost single loops). This may be important to flow and other fast loops.
. You may have a better "non-continuous" conditions management, including some logic to treat special batch conditions.

Some positive points for the single loops:
. Reliability: a failure in one controller will not stop all the system
. Maintenance: every controller have one input, one output, display, keyboard, and you don't need special cable or software to program/debug it. An instrumentist can fix a problem at saturday 3AM.

Regards

Marcos T. B.
 
I have replaced single loop controlers with PLC's for years. I need to switch between different controlers during the process.I also pass values and control bits between loops. The input and output configurations vary but I maintain a structured data block for each controler. This makes HMI screens and historical base management easy for multiple loops. With newer PLC's this is also possible with multi-instance processing.In many cases the HMI database can be populated straight from the PLC. I am now starting a project with S-7 and IFIX and am searching for peoples experience with Siemens PID controlers. In the past I have used other brands or written my own.
 
S

Steve Hartigan

Siemens purchased Moore Automation over five years ago. They still market their 353 Controllers which I found to be the most robust and advanced devices available. That said, they are a bit pricier than some others on the market. At an LNG plant that I previously worked at, they were the sole control platform on several heat exhangers and boiler controls.

I was recently told that Emerson (Fisher-Rosemount) is no longer making their model. I have heard good things about the Foxboro products, but have never seen them in action. I hope that this helps.
 
D

Dennis Patterson

I would suggest using loops in the PLC, it is more cost effective, easy to do and scalable. In the Boral cement plant i work at, i add and remove loops all day. If the process engineer wants to cascade a temperature and flow loop its simple to perform in the PLC without tedious wiring and saves days of work at a time. We have hundreds of loops running in the PLC to SCADA, using S7 and TI with CITECT. If you want an example just e-mail me and ill send you a S7 example.