We have a Frame 6 machine with MkV control system. We are experiencing high GT spread and we are unable to point out the root cause of the problem.
Following were observed:
1) High temperture is mostly in the thermocouple 9 & 13 even after replacing / swapping the fuel nozzles.
2) Erratic reading was observed in thermocouple 9 wherein the reading suddenly reduces drastically and immediately after that it comes back to normal.
3) We have presently disconnected the thermocouple 9 because of erratic readings.
4) Following is the thermocouple readings before disconnecting thermocouple 9:
( From 1 to 18 thermocouple)
521
522
524
524
526
529
533
538
411
553
562
561
559
558
555
548
537
526
TTXM 539Deg C
CTD 333 Deg C
5) Readings after disconnecting the thermocouple 9
( From 1 to 18 thermocouple)
547
542
544
559
547
568
593
602
-83
613
591
598
592
570
564
564
562
548
TTXM 572Deg C
CTD 353 Deg C
Following were observed:
1) High temperture is mostly in the thermocouple 9 & 13 even after replacing / swapping the fuel nozzles.
2) Erratic reading was observed in thermocouple 9 wherein the reading suddenly reduces drastically and immediately after that it comes back to normal.
3) We have presently disconnected the thermocouple 9 because of erratic readings.
4) Following is the thermocouple readings before disconnecting thermocouple 9:
( From 1 to 18 thermocouple)
521
522
524
524
526
529
533
538
411
553
562
561
559
558
555
548
537
526
TTXM 539Deg C
CTD 333 Deg C
5) Readings after disconnecting the thermocouple 9
( From 1 to 18 thermocouple)
547
542
544
559
547
568
593
602
-83
613
591
598
592
570
564
564
562
548
TTXM 572Deg C
CTD 353 Deg C