Microcontroller based PID controller

Hi all,
This is my firs post in this forum.
I design simple PID controller (programing Microchip PIC18F2550) based on theory I have learned from Control system on college. I am newbie in PID control, so I am sorry if I ask something what is simple.

I would like whether my controller was designed correctly.
Description:
Heater element 24V 40W is in the aluminum heat sink with blades (size 6cm x 6cm x 1cm block plus 5 blades height 3cm). The temperature is controlled by micro-controller (the PID controller is programmed in the micro-controller) by 19.5V PWM (power source used from old laptop).

Output of the controller is sum of P-control, I-control and D-control. The sign of the output signal is given by the sum of those three control signals. (positive sign = heater is ON, negative sign = heater is OFF - heat sink is cooled by ambient air ). The output (sum of P-control, I-control and D-control) is fed in to PWM 10bit register. So value 0 = 0%PWM Duty cucle and 1023 = 100%PWM Duty cycle. For instance if PID controller output is 767, then PWM Duty cycle is set o 75%. If PID output is 1500 (it is more than 1023) then PWM regisr is set to 1023 (100% PWM).
Ths is how I set the realtion beteen the output signal and power signal for heater element.
Q1: Is that way right or it should be done different way?


The PID controller looks works fine, but I have one problem and I do not know whether it is normal for PID controller or not.
After many tuning tests, I have find out that if I tune the PID controller to reach e.g. 80°C from ambient temperature (system is turned ON) the setpoint is reached with no or very small overshoot, but it regulates the temperature around set-point (+5°C -5°C) slowly - response is slow.

If I tune the PID controller to control the temperature relatively fast around the set-point (+5°C -5°C), regulation works fine around setpoint Picture 2, but at system start up the temperature raise very high over 80°C (up to 120°C and it was still raising even the integral output has started to decrease Picture 1) due to very high integral control output value (area from 20°C up to 80°C is huge what causes that Integral value build up at 80°C up to around 1000 (97%PWM), so heater power 97%.

Picture 1
Picture 1.png



Picture 2
Picture 2.png




So there are two options for controller tuning
a) Controller is tuned to reach 80°C from ambient temperature with very tiny overshoot
or
b) Controller is tuned to control the temperature around 80°C

Is this behaviour normal for PID controller or not and my program code is incorrect?


This is the way how I calculate the output of my PID controller:
Error
Error = Set-point - Current temp. (Error is positive if the measured temperature is below the set-point and negative if it is above the set-point)

Proprotional
Proportional output = Error * Kp
(Prop. output sign depend on error sign)

Integral
Integral output = Accumulated integral "strips" * Ki
(where Ki is integral parameter entered by user)
where
Accumulated integral "strips" = Accumulated integral "strips" + Actual integral strip
Actual integral "strip" = ( (Measured current error - Previous error)/2 ) * T (T= sampling period = 2 seconds), (sign of one integral "strip" depend on Error sign)
Picture 3
Picture 3.png




Derivative
Derivative output = ( (Measured current error - Previous error) / T )* Kd
(T= sampling period = 2 seconds)
The sign of the derivative output is:
1. tempereture bellow setpoint and falling toward setpoint (error decrease) - negative
2. tempereture above setpoint and raising from setpoint (error inrease)- positive
3. tempereture above setpoint and falling toward setpoint (error inrease)- negative
4. tempereture bellow setpoint and raising from setpoint (error inrease)- positive
Picture 4
Picture 4.png



Q2: Is this PID controller design correct?

Many thanks for help.
 
Dave, thanks for reply.

Yes, you are right Dave. This project is "school presentation project" where I will present different type of controls (P only, PI, PD, PID) and explain which control is best for my plant.

But my problem is that I am designing the PID controller as a program in the microprocessor PIC18F2550.
So I am not sure, whether that behavior (integral control is very high at set-point when system starts up from 20° to 80°C, so it cause that temperature raise up to 120°C) is normal and I have to apply Anti-windup system, or that behavior should not happen and I should to review my PID control equation (program) in micro-controller and check what is wrong there.
By othere words, I need to know whether to fix my program or introduce anti wind up algorithm for system start up.
 