In this machine center, all real-world inputs are N.O. proximity sensors arranged along a conveyor line.
Describe all combinations of inputs that would allow the output to energize.
This is a simple answer: the input must be energized (in other words, an object is detected in front of the sensor) for the output to become energized.
In all exercises, the sensors are assumed to be either inductive, capacitive, or light-on optical proximity switches, with either NPN or PNP wiring. Each problem will specify whether they are normally open (N.O.) or normally closed (N.C.) contacts.
Remember this important difference between logic and circuits. Any real-world device, whether N.O. or N.C. can be programmed in the PLC to energize an output. Do not worry about whether the real-world device is N.C. or N.O., but rather, try to identify the conditions that will allow current to flow through the device or not, which will influence its behavior in the logic.
The computer will not recognize any difference between an N.O. device versus an N.C. device with an object in front of it, therefore, both situations would appear identical to the PLC.
Even if current is not flowing through the input device, the output device may still become energized through a proper sequence of logic instructions. This is very different from purely electrical circuits.
In this machine center, all real-world inputs are N.C. proximity sensors arranged along a conveyor line.
The input must be de-energized (no object detected; the area in front of the sensor is clear) for the output to become energized.
The input must be de-energized (no object detected) for the output to become energized.
The input must be energized (detecting an object) for the output to become energized.
Remember: These are normally open devices!
Inputs 1-3 must be energized (detecting an object), and input 4 must be de-energized (no object detected) in order for the output to energize.
Remember: These are normally closed devices!
Inputs 1-3 must be de-energized (no object detected), and input 4 must be energized (detecting an object) in order for the output to energize.
Two possible combinations allow the output to be energized:
Inputs 1 and 3 must be energized (detecting an object), while inputs 2 and 4 could be in either state.
OR
Inputs 2 and 4 must be de-energized (no object detected), while inputs 1 and 3 could be in either state.
Inputs 1 and 3 must be de-energized (no object detected), while inputs 2 and 4 could be in either state.
OR
Inputs 2 and 4 must be energized (detecting an object), while inputs 1 and 3 could be in either state.
Remember: These are normally Open devices!
All inputs must be de-energized (no object detected) in order for the output to energize.
Remember: These are normally Closed devices!
All inputs must be energized (detecting an object) in order for the output to energize.
A series of real-world N.C. emergency stop (E-Stop) devices must keep an output motor contactor energized unless any one of the buttons is pressed.
If these N.C. E-stop buttons are connected to a safety PLC input module, how should the ladder logic rung be designed to keep the output energized until any button is pressed?
Remember: N.O. contacts will energize only when electricity is flowing into the input.
When a normally closed button is un-pressed, electricity is flowing.
In this way, the PLC is ‘tricked’ into thinking we have standard N.O. pushbuttons that are being pressed.
‘Tricking’ is, perhaps, the wrong way to explain the situation since the programming is quite reliable, but this problem illustrates why we must think of the PLC logic in terms of the electrical continuity of the real-world devices.
In both cases. Input 1 must be energized (detecting an object) and input 4 must be de-energized (no object detected).
Beyond this, input 2 must be de-energized (no object detected), and input 3 does not matter.
OR
Input 3 must be energized (detecting an object), and this time, input 2 does not matter.
In both cases. Input 1 must be de-energized (no object detected) and input 4 must be energized (detecting an object).
Beyond this, input 2 must be energized (detecting an object), and input 3 does not matter.
OR
Input 3 must be de-energized (no object detected), and this time, input 2 does not matter.
Published under the terms and conditions of the Creative Commons Attribution License
by Seth Price