Electricity and Electronics
Troubleshooting Electrical Devices
10 questions
Page 1 of M03d478b72a271d2b450124b08e12daad2 0 of 10 answers revealed (0%)
  • Question 1 of 10
    A normally open (NO) pushbutton is connected to a control relay in a 24 volt DC circuit.
    The circuit fault is a broken wire between the pushbutton and the relay coil. What voltages should be measured at each lettered point (with respect to ground)?
    Reveal answer
  • Question 2 of 10
    The circuit fault is a broken DC power supply. What voltages should be measured at each lettered point (with respect to ground)?
    Reveal answer
  • Question 3 of 10
    The circuit fault is a broken spring return in the pushbutton - always closed. What voltages should be measured at each lettered point (with respect to ground)?
    Reveal answer
  • R
    robb_IE July 24, 2026
    You should specify which two points are being measured. You can’t measure voltage of a single point.
    • D
      David Peterson July 24, 2026
      You are correct. The questions have been updated to state that all voltages are meant to be relative to ground. And we'll assume it's a typical grounded (-) power supply.
  • N
    Nutsandbolts July 25, 2026
    On question 3 some voltage should be measured different from 0v.